An air handling unit (AHU) motor in a hotel consumes 32 KW of real power
and being supplied with 35.5 kVA of apparent power, Determine;
(a) the reactive power drawn by the motor,
(Ans: 15.37 KVAn
(b) the power factor of the motor,
(Ans: 0.9014 )
ame: Kon Kim Hon Class: A
An air handling unit (AHU) motor in a hotel consumes 32 KW of real power
and being supplied with 35.5 kVA of apparent power, Determine;
(a) the reactive power drawn by the motor,
(Ans: 15.37 KVAn
(b) the power factor of the motor,
(Ans: 0.9014 )
Ask by Powell Hart. in Singapore
Dec 09,2024
Solución de inteligencia artificial de Upstudy
Respuesta verificada por el tutor
Responder
(a) The reactive power drawn by the motor is approximately 15.37 kVAR.
(b) The power factor of the motor is approximately 0.9014.
(b) The power factor of the motor is approximately 0.9014.
Solución

¡Inicia sesión para desbloquear respuestas gratis!
Una plataforma de aprendizaje en la que confían millones de estudiantes y profesores reales.

Respondido por UpStudy AI y revisado por un tutor profesional
Como
Bonus Knowledge
To find the reactive power drawn by the motor, we can use the formula:
, where
is the apparent power (35.5 kVA) and
is the real power (32 kW). Plugging in the values, we calculate the reactive power and discover that the motor draws approximately 15.37 kVAr.
For the power factor, we divide the real power by the apparent power:
, or
, which results in a power factor of 0.9014. This indicates that around 90% of the power utilized is effective in doing real work, which is quite efficient for an air handling unit!