A 30 A circuit breaker is used to protect a 22 A electrical load. If the circuit is totally enclosed in thermal insulation and has a Ca of 0.88, what is the minimum current carrying capacity (Iz) for this conductor?

Ask by Schofield Brooks. in Singapore
Jan 20,2025

Real Tutor Solution

Tutor-Verified Answer

Answer

The minimum current carrying capacity (\( I_z \)) for the conductor is approximately 31.25 A.

Solution

To determine the minimum current carrying capacity (\( I_z \)) for the conductor protecting a 22 A electrical load with a 30 A circuit breaker, while considering the thermal insulation factor (\( C_a \)) of 0.88, follow these steps: ### 1. Determine if the Load is Continuous Assuming the 22 A load is **continuous** (operating for three hours or more), the National Electrical Code (NEC) requires that the conductor ampacity be **125%** of the continuous load. This accounts for potential overheating under prolonged use. \[ \text{Adjusted Load} = 1.25 \times \text{Load} = 1.25 \times 22\,\text{A} = 27.5\,\text{A} \] ### 2. Apply the Correction Factor Since the conductor is **totally enclosed in thermal insulation**, a correction factor (\( C_a \)) of 0.88 is applied to the adjusted load to account for reduced heat dissipation. \[ I_z = \frac{\text{Adjusted Load}}{C_a} = \frac{27.5\,\text{A}}{0.88} \approx 31.25\,\text{A} \] ### 3. Select the Appropriate Conductor Size Conductor sizes are standardized. Therefore, round up to the next standard size to ensure safety and compliance. The next standard size after 31.25 A is typically **35 A**. ### **Conclusion** The **minimum current carrying capacity (\( I_z \))** for the conductor should be **at least 31.25 A**. In practice, you would select the next standard conductor size, such as 35 A, to comply with safety standards and ensure adequate protection. **Final Answer:** A minimum conductor capacity of approximately 31.25 A is required.

Reviewed and approved by the UpStudy tutoring team

error msg
Explain
Simplify this solution

Extra Insights

To find the minimum current carrying capacity (\(I_z\)) for the conductor, we can apply the formula: \[ I_z = \frac{I_{load}}{C_a} \] Given: - \(I_{load} = 22 A\) - \(C_a = 0.88\) Plugging in the values: \[ I_z = \frac{22 A}{0.88} \approx 25 A \] Thus, the minimum current carrying capacity for this conductor is approximately 25 A, which ensures safe operation while considering the thermal insulation's effect. Now, let’s explore the historical background of circuit breakers. The first circuit breakers were invented in the late 19th century as a safety device to prevent overcurrents, much like fuses but with the added benefit of being resettable. As electrical loads grew with the advent of new appliances, circuit breakers evolved to handle more complex circuitry, contributing significantly to modern electrical safety. For real-world applications, circuit breakers are crucial in residential, commercial, and industrial settings. They not only protect wiring and devices from damage but also enhance safety by preventing electrical fires. Properly sized circuit breakers prevent nuisance tripping while ensuring that an overcurrent doesn't lead to severe damage or hazards.

Try Premium now!
Try Premium and ask Thoth AI unlimited math questions now!
Maybe later Go Premium
Study can be a real struggle
Why not UpStudy it?
Select your plan below
Premium

You can enjoy

Start now
  • Step-by-step explanations
  • 24/7 expert live tutors
  • Unlimited number of questions
  • No interruptions
  • Full access to Answer and Solution
  • Full Access to PDF Chat, UpStudy Chat, Browsing Chat
Basic

Totally free but limited

  • Limited Solution
Welcome to UpStudy!
Please sign in to continue the Thoth AI Chat journey
Continue with Email
Or continue with
By clicking “Sign in”, you agree to our Terms of Use & Privacy Policy