- **Starting Current:** Approximately 89 A
- **Full Load Torque:** Approximately 88 Nm
- **Switching Devices:** Use contactors rated at least 125 A
- **Cables/Wires:** 6 mm² copper conductors
- **Protective Devices:** 40 A circuit breaker
Solución
To determine the various parameters for the given three-phase squirrel cage induction motor, we'll systematically approach each part of the problem.
### **Given Data:**
- **Rated Power (Prated):** 15 kW
- **Line Voltage (VL):** 400 V
- **Frequency (f):** 50 Hz
- **Number of Poles (p):** 4
- **Efficiency (η):** 88% (0.88)
- **Power Factor (pf):** 0.8 (lagging)
- **Slip (s):** 4% (0.04) for part (ii)
---
### **Part (i): Starting Current with Star/Delta Starter**
**Approach:**
1. **Calculate Full-Load Current (Irated):**
The apparent power \( S \) is given by:
\[
S = \frac{P_{\text{rated}}}{\eta \times pf} = \frac{15,000\,\text{W}}{0.88 \times 0.8} \approx 21,306\,\text{VA}
\]
For a three-phase system:
\[
S = \sqrt{3} \times V_L \times I_{\text{rated}}
\]
\[
I_{\text{rated}} = \frac{S}{\sqrt{3} \times V_L} = \frac{21,306}{1.732 \times 400} \approx 30.78\,\text{A}
\]
2. **Determine Starting Current for Star/Delta Starter:**
The starting current for a Direct-On-Line (DOL) starter is given as a multiple of the rated current (starting factor = 5):
\[
I_{\text{start,DOL}} = 5 \times I_{\text{rated}} = 5 \times 30.78 \approx 153.9\,\text{A}
\]
A star/delta starter reduces the starting voltage to \( \frac{V_L}{\sqrt{3}} \), thereby reducing the starting current by the same factor:
\[
I_{\text{start,SD}} = \frac{I_{\text{start,DOL}}}{\sqrt{3}} \approx \frac{153.9}{1.732} \approx 88.8\,\text{A}
\]
**Answer:**
The starting current when using a star/delta starter is approximately **89 A**.
---
### **Part (ii): Full Load Torque at 4% Slip**
**Approach:**
1. **Determine Synchronous Speed (Ns):**
\[
N_s = \frac{120 \times f}{p} = \frac{120 \times 50}{4} = 1500\,\text{RPM}
\]
2. **Determine Actual Speed (N):**
\[
N = N_s \times (1 - s) = 1500 \times (1 - 0.04) = 1440\,\text{RPM}
\]
3. **Calculate Mechanical Power Output (Pmech):**
\[
P_{\text{mech}} = P_{\text{rated}} \times \eta = 15,000\,\text{W} \times 0.88 = 13,200\,\text{W}
\]
4. **Determine Angular Speed (ω):**
\[
\omega = \frac{2\pi N}{60} = \frac{2\pi \times 1440}{60} = 48\pi\,\text{rad/s} \approx 150.8\,\text{rad/s}
\]
5. **Calculate Torque (T):**
\[
T = \frac{P_{\text{mech}}}{\omega} = \frac{13,200}{150.8} \approx 87.5\,\text{Nm}
\]
**Answer:**
The full load torque at 4% slip is approximately **88 Nm**.
---
### **Part (iii): Size of Switching Devices**
**Approach:**
- **Switching devices** (like contactors) must handle the maximum current. Since the starting current with a star/delta starter is approximately **89 A**, the contactor should be rated above this value to ensure reliability and safety.
- **Common Practice:** Use a safety margin, often **125%** of the maximum expected current.
\[
\text{Contactor Rating} \geq 1.25 \times 89\,\text{A} \approx 112\,\text{A}
\]
However, commercially available contactors typically come in standard sizes such as 100 A or 125 A. Given that 100 A is slightly below, it's prudent to opt for a **125 A** contactor.
**Answer:**
Use contactors (switching devices) rated for at least **125 A**.
---
### **Part (iv): Size of Cables/Wires**
**Approach:**
- The conductor size must accommodate the **full-load current** of approximately **31 A**.
- **Using Standard Ampacity Tables:**
- For copper conductors, a **6 mm²** cross-sectional area is typically rated for up to **36 A**, which provides a comfortable margin for 31 A.
**Answer:**
Employ **6 mm²** copper conductors for the motor’s cables/wires.
---
### **Part (v): Size of Protective Devices**
**Approach:**
1. **Determine Protective Device Rating:**
- Protective devices (like circuit breakers) are usually sized at **125%** of the full-load current to allow for normal operation without nuisance tripping.
- \[
\text{Breaker Rating} = 1.25 \times 31\,\text{A} \approx 39\,\text{A}
\]
2. **Consider Motor Starting:**
- Since a star/delta starter reduces the starting current, the protective device must tolerate up to **89 A** momentarily without tripping.
- **Solution:** Use a breaker with **thermal-magnetic** characteristics that can handle higher inrush currents temporarily.
**Answer:**
Use a protective circuit breaker rated at approximately **40 A** to ensure proper protection without tripping during startup.
---
### **Summary of Answers:**
1. **Starting Current with Star/Delta Starter:** ~89 A
2. **Full Load Torque at 4% Slip:** ~88 Nm
3. **Size of Switching Devices:** Contactors rated at least 125 A
4. **Size of Cables/Wires:** 6 mm² copper conductors
5. **Size of Protective Devices:** 40 A circuit breaker